Hi Dave,
Not sure I understand, but if the ModBus address is 2000 why not try 2000?
Message: 7214 |
Date: 4/10/2013 |
| Subject: Re: Modbus Addressing |
The ones that are 2000 are working with E2 00
What is the E in the front?
Dave
> Hi Dave,
> From: daves3891 <fahque99@...>
> Sent: Tuesday, April 9, 2013 2:34 PM
> Subject: [DynoMotion] Modbus Addressing
> I am having trouble understanding the modbus addressing with a Click PLC.
> I have the input/output working on the base CPU with the following addresses
> {"\x01\x04\xE0\x00\x00\x01", 6, 0} Input
> {"\x01\x10\xE2\x00\x00\x01", 6, 1} Output
> {"\x01\x10\xE4\x00\x00\x01", 6, 3} Internal Coil
> And if I understand the comments properly then the E0 00 is the in address and the E2 00 is the out address E4 00 is the internal coil address.
> Where I am having the problem is with additional modules.
> The CPU has the Y001-Y006 (Modbus 2000) Kflop - E200
> And I have 7 modules attached with output starting at
> Y401-Y408 (modbus 2080) Kflop - ?
> Y501-Y508 (modbus 20A0) Kflop - ?
> Y601-Y608 (modbus 20C0) Kflop - ?
> I have tried E280, E2A0, E2C0, E208, E20A, E20C but none seem to work.
> What am I missing here?
> Thanks
> Dave
Message: 7215 |
Date: 4/10/2013 |
OK, I got it working
Modbus HEX 2080 = Kflop E2 08
Modbus HEX 20A0 = Kflop E2 0A
Modbus HEX 20C0 = Kflop E2 0C
Modbus HEX 20E0 = Kflop E2 0E
Dave
> Thanks