One possibility is that the system is
configured to move faster than your power supply/amplifiers/motors allow.
If the motion trajectory is too fast the output will saturate at maximum, the
motors will fall behind, and only after the trajectory stops will the motors be
able to catch up usually with a large overshoot.
Normally this situation would trip an
immediate following error fault. But possibly you have the Max Following Error
set to a very large value.
If you make a large move using the Step Response
Screen you should see all this: Output saturates at max, Position falling
behind, finally catching up and overshooting. Or if something else is
happening you should be able to see it also.
First check that your “Max limits - Output”
parameter is set to 2047 to allow Kanalog to output full +/-10V to the
amplifiers.
G0 and Jog commands are performed as “S”
shape (jerk limited) motions controlled by the settings in the Step Response
Screen in the KMotion.exe program. Check that the Max Vel is set
reasonably for your system (also Accel and Jerk).
I hope this helps.
Message: 65 |
Date: 10/18/2009 |
| Subject: Re: Fast movements |
This problem i solved.
I have belived that i should use encoders with as high count as possible. I was using ecoders with 41615 counts / inch.
Today i set them down to just over 10160 counts / inch and my machine got much faster and become more stable than ever. Afer ajusting my setup. I went from 0.2 in p to 3.5 now
No more overshooting
--- In DynoMotion@yahoogroups.com, "TK" <tk@...> wrote:
> One possibility is that the system is configured to move faster than your
> power supply/amplifiers/motors allow. If the motion trajectory is too fast
> the output will saturate at maximum, the motors will fall behind, and only
> after the trajectory stops will the motors be able to catch up usually with
> a large overshoot.
> Normally this situation would trip an immediate following error fault. But
> possibly you have the Max Following Error set to a very large value.
> If you make a large move using the Step Response Screen you should see all
> this: Output saturates at max, Position falling behind, finally catching up
> and overshooting. Or if something else is happening you should be able to
> see it also.
> First check that your "Max limits - Output" parameter is set to 2047 to
> allow Kanalog to output full +/-10V to the amplifiers.
> G0 and Jog commands are performed as "S" shape (jerk limited) motions
> controlled by the settings in the Step Response Screen in the KMotion.exe
> program. Check that the Max Vel is set reasonably for your system (also
> Accel and Jerk).
> I hope this helps.
> _____
> From: DynoMotion@yahoogroups.com [mailto:DynoMotion@yahoogroups.com] On
> Behalf Of s.astrom
> Sent: Saturday, October 17, 2009 2:03 AM
> Subject: [DynoMotion] Fast movements
> When i jog or use GO the table does not just make a quick halt when done. It
> moves past the stop point and then reverses i few mm then halts.
> What parameter should i change to correct this?
> This only happens when i use rappid movements